Re: Datenexport
Posted: Sat Feb 08, 2025 3:27 pm
by JKW
Thank you - it kind of worked, but somehow I'm also lost because I don't know what the downloaded data means. ‘sn’ and 'time' is easy, but the other data is useless to me if I don't have a description. Where can I find such a legend/definition/description for the data?
It is about the following data:
protocol, masterState, etoday, generation, input, meterPowerR, meterPowerS, meterPowerT, generationPower, loadsPowerR, loadsPowerS, loadsPowerT, RVolt, RCurrent, RPower, RFreq, SVolt, SCurrent, SPower, SFreq, TVolt, TCurrent, TPower, TFreq, pv1Volt, pv1Current, pv1Power, pv2Volt, pv2Current, pv2Power, pv3Volt, pv3Current, pv3Power, pv4Volt, pv4Current, pv4Power, pv5Volt, pv5Current, pv5Power, pv6Volt, pv6Current, pv6Power, pv7Volt, pv7Current, pv7Power, pv8Volt, pv8Current, pv8Power, pv9Volt, pv9Current, pv9Power, pv10Volt, pv10Current, pv10Power, pv11Volt, pv11Current, pv11Power, pv12Volt, pv12Current, pv12Power, pv13Volt, pv13Current, pv13Power, pv14Volt, pv14Current, pv14Power, pv15Volt, pv15Current, pv15Power, pv16Volt, pv16Current, pv16Power, pv17Volt, pv17Current, pv17Power, pv18Volt, pv18Current, pv18Power, pv19Volt, pv19Current, pv19Power, pv20Volt, pv20Current, pv20Power, pv21Volt, pv21Current, pv21Power, pv22Volt, pv22Current, pv22Power, pv23Volt, pv23Current, pv23Power, pv24Volt, pv24Current, pv24Power, invTemperation, ambientTemperation, boostTemperation, dspTemprature, epsVoltR, epsCurrentR, epsPowerR, epsVoltS, epsCurrentS, epsPowerS, epsVoltT, epsCurrentT, epsPowerT, epsPower, todayYield, fault1, fault2, fault3, fault4, fault5, fault6, fault7, fault8, masterState, meterPower, meterPower2, meterStatus, meter2Status, cellTemperatureHigh, cellTemperatureLow, cellVoltageHigh, cellVoltageLow, cellVoltageHighHighPrecision, cellVoltageLowHighPrecision, epsFrequency, powerFactory, efficiency, batVolt, batCurrent, meterPowerR, meterPowerS, meterPowerT, meter2PowerR, meter2PowerS, meter2PowerT, dspTemprature, invInput, pvInputNumber, eTotaltime, powerFactory, reactivePower, apparentPower, peMonitoringFlag, cloudControlled, model, groupEnable, hostStandby, slaverNumber, feedinTotalTime, epsRunTotalTime, epsRunTimes, operatingMode, SystemInvNum, batTemperation, feedin, gridConsumption, loads, Meter1Power, paralGridPower, ExOutputPower, ARMActivelyReportsMessageEntries, ARMResponseMessageEntry, ControlledSlaverState, paralMeterPower2, SwitchState, isHistory
Re: Datenexport
Posted: Sun Feb 09, 2025 10:31 am
by Dave Foster
JKW wrote: Sat Feb 08, 2025 3:27 pm
Thank you - it kind of worked, but somehow I'm also lost because I don't know what the downloaded data means. ‘sn’ and 'time' is easy, but the other data is useless to me if I don't have a description. Where can I find such a legend/definition/description for the data?
It is about the following data:
protocol, masterState, etoday, generation, input, meterPowerR, meterPowerS, meterPowerT, generationPower, loadsPowerR, loadsPowerS, loadsPowerT, RVolt, RCurrent, RPower, RFreq, SVolt, SCurrent, SPower, SFreq, TVolt, TCurrent, TPower, TFreq, pv1Volt, pv1Current, pv1Power, pv2Volt, pv2Current, pv2Power, pv3Volt, pv3Current, pv3Power, pv4Volt, pv4Current, pv4Power, pv5Volt, pv5Current, pv5Power, pv6Volt, pv6Current, pv6Power, pv7Volt, pv7Current, pv7Power, pv8Volt, pv8Current, pv8Power, pv9Volt, pv9Current, pv9Power, pv10Volt, pv10Current, pv10Power, pv11Volt, pv11Current, pv11Power, pv12Volt, pv12Current, pv12Power, pv13Volt, pv13Current, pv13Power, pv14Volt, pv14Current, pv14Power, pv15Volt, pv15Current, pv15Power, pv16Volt, pv16Current, pv16Power, pv17Volt, pv17Current, pv17Power, pv18Volt, pv18Current, pv18Power, pv19Volt, pv19Current, pv19Power, pv20Volt, pv20Current, pv20Power, pv21Volt, pv21Current, pv21Power, pv22Volt, pv22Current, pv22Power, pv23Volt, pv23Current, pv23Power, pv24Volt, pv24Current, pv24Power, invTemperation, ambientTemperation, boostTemperation, dspTemprature, epsVoltR, epsCurrentR, epsPowerR, epsVoltS, epsCurrentS, epsPowerS, epsVoltT, epsCurrentT, epsPowerT, epsPower, todayYield, fault1, fault2, fault3, fault4, fault5, fault6, fault7, fault8, masterState, meterPower, meterPower2, meterStatus, meter2Status, cellTemperatureHigh, cellTemperatureLow, cellVoltageHigh, cellVoltageLow, cellVoltageHighHighPrecision, cellVoltageLowHighPrecision, epsFrequency, powerFactory, efficiency, batVolt, batCurrent, meterPowerR, meterPowerS, meterPowerT, meter2PowerR, meter2PowerS, meter2PowerT, dspTemprature, invInput, pvInputNumber, eTotaltime, powerFactory, reactivePower, apparentPower, peMonitoringFlag, cloudControlled, model, groupEnable, hostStandby, slaverNumber, feedinTotalTime, epsRunTotalTime, epsRunTimes, operatingMode, SystemInvNum, batTemperation, feedin, gridConsumption, loads, Meter1Power, paralGridPower, ExOutputPower, ARMActivelyReportsMessageEntries, ARMResponseMessageEntry, ControlledSlaverState, paralMeterPower2, SwitchState, isHistory
Many of those will be self explanatory, there is a variable table listed here
https://www.foxesscloud.com/public/i18n ... ent.html#7 but it may not provide a lot more useful information as some things are for Fox use i.e. 'ARMResponseMessageEntry', 'fault1...8
Where you have a PV (solar) string you will get 3 values - volts, current and power these are real time values and the most useful is power as that tells you how much power you were generating at any one moment.
You then have the same for each of the three phases these are named R (for reference), S (for secondary) and T (for tertiary) and for each you will see frequency, volts, power and current.
Likewise you have your load power for each of the 3 phases
Your meter is not terribly useful (it is what measurements the inverter reads) but you might find it useful.
You have cell low and high voltages (not terribly useful)
You have cell low and high temperatures (very useful as the cell low temperature is what the BMS throttles the charge/discharge with if it is low).
batTemperation is the temperature recorded by the BMS (not very useful)
The useful temperature readings are the cell low and high, InvTemperation (the temp of the cooling fins on the back) and ambientTemperature (the internal temperature of the inverter)
feedin is the running total of all export, loads the running total of load power
generationpower is the inverters output negative is charge, positive is output
today yield total of all inverter output (either from solar, grid or battery) for today
EPS values are for the Emergency Power Supply all 3 phases (if fitted)