Does anybody knows what "Safety Invalid" means on the screen. Our whole system is disconnected from the grid since more than a week. Technical Support from the installer has no clue or they do not react.
Means you need to set the inverter to say G98 or G9 for UK under Settings > 0000 > Feature > Safety