Posted: Tue Apr 29, 2025 6:28 pm
Reposted in this section 29/04.
Hi all,
My system: 7 x 440 PV. H1-3.7-E-G2. 1 x EP11. Work Mode Self Use.
I ran my ASHP to top up DHW at noon today (a short cycle from 33' back up to 43') Battery indicating 100% and lots of PV coming in.
When the water heating was complete the battery level was indicating 99%. Then a while later 98%. Subsequently, most PV energy was diverted to the grid -I was expecting the battery to be prioritised before exporting but that never happened. Three hours later at 5 pm there was 1.13kW PV incoming, of which 12w was to the battery (still at 98%) house 0.11kW and 1.01kW to the grid. Battery temperature was 18.5'. Prior to today I've always seen the battery go back to 100% pretty rapidly in sunshine, today it remained at 98%.
Any comments/observations/tips would be welcome. I've only been using the system for a week, please make allowances! Thanks.
Note from 29/04: Same behaviour today. Battery not charging from solar after heating water. System seems to be prioritising export to grid.
Hi all,
My system: 7 x 440 PV. H1-3.7-E-G2. 1 x EP11. Work Mode Self Use.
I ran my ASHP to top up DHW at noon today (a short cycle from 33' back up to 43') Battery indicating 100% and lots of PV coming in.
When the water heating was complete the battery level was indicating 99%. Then a while later 98%. Subsequently, most PV energy was diverted to the grid -I was expecting the battery to be prioritised before exporting but that never happened. Three hours later at 5 pm there was 1.13kW PV incoming, of which 12w was to the battery (still at 98%) house 0.11kW and 1.01kW to the grid. Battery temperature was 18.5'. Prior to today I've always seen the battery go back to 100% pretty rapidly in sunshine, today it remained at 98%.
Any comments/observations/tips would be welcome. I've only been using the system for a week, please make allowances! Thanks.
Note from 29/04: Same behaviour today. Battery not charging from solar after heating water. System seems to be prioritising export to grid.