Battery not supplying full load overnight
Posted: Mon Aug 04, 2025 2:36 pm
Hi all,
I just solar installed with KH7 inverter and an EP11 battery.
I've noticed that when the solar is producing enough to cover the load, everything looks fine - house load gets covered and the excess is exported. However, overnight I see a near constant 180-200W import from the grid (according to the smart meter/octopus mini) and only the remaining is supplied from the battery.
Given that the overnight load is about 280-320W, only about a third is of the power is supplied by the battery. The FoxCloud app reports a load of 100W or so.
The numbers seem to add up, but why would the battery not be used for the majority of the load?
Thanks for any help in advance!
I just solar installed with KH7 inverter and an EP11 battery.
I've noticed that when the solar is producing enough to cover the load, everything looks fine - house load gets covered and the excess is exported. However, overnight I see a near constant 180-200W import from the grid (according to the smart meter/octopus mini) and only the remaining is supplied from the battery.