Off grid setup with model: H1-5.0-E-G2
Posted: Sat Sep 20, 2025 10:05 pm
by foxuser8876
Hello Fox ESS Community,
I am considering installing a Fox H1 Gen2 hybrid inverter (model: H1-5.0-E-G2) in a location where there is no grid connection available. I have the following questions:
Does this firmware version support commissioning the inverter without any grid connection (i.e., no grid present at any point during setup)?
If full grid-less commissioning is not officially supported, is there a firmware version or installer method that allows it?
If a temporary grid reference (e.g., generator or test supply) is needed for setup, what is the recommended procedure, and can it be removed afterward for fully off-grid operation?
Are there any warranty or safety implications if the inverter is commissioned without grid?
Additionally, I would appreciate any guidance on settings for running the inverter fully off-grid using EPS mode once installed.
Thank you very much for your assistance.
Re: Off grid setup with model: H1-5.0-E-G2
Posted: Mon Sep 22, 2025 3:51 pm
by Will
Yes, once all connected you can manually start the inverter from solar or by pressing the blackstart button/process on the battery and the inverter will wake up to be commissioned and provide power on the EPS port assuming EPS port is enabled on UPS mode.