H1-3.7-E — repeated "Grid Voltage Fault
Posted: Thu Sep 17, 2026 2:14 pm
H1-3.7-E, 4x Mira HV25, 10x Trina 425W, installed Apr 2023, G98,
firmware 1.63/1.02/1.70.
Not the fault in the "Error Code 28 / Vac 10min Avg" thread — my fault
register reports "Grid Voltage Fault" (instantaneous), never "Grid 10min
Voltage Fault". They're separate bits in the same word. I proved the
10-min rule isn't my trigger: over today's 05:36-14:07 window the
sliding 10-min average was above 253V in 243/243 windows (and above 255V
in 88%). If that rule were tripping me I'd be in permanent fault, not
intermittent. So raising Vac 10min Avg 253->255 does nothing for me.
What I actually see:
- Trips occur at 259-263V instantaneous. ~100 trips on 17 Sep, 131 min
off-grid, first trip 02:08 (pitch dark — no export).
- 74.9% of all 28,723 hours since Jun 2023 had a max above 253V.
7.0% above 258V. 29 hours above 262V. All-time max 264V (17 Sep 2026).
- The night voltage is WORSE than the solar-peak voltage: 00:00-04:59
mean 255.5V vs 10:00-15:59 mean 253.2V. Nothing to do with my export —
it's over-voltage at 3am with the panels producing nothing.
DNO (Northern Powergrid) visited, measured, agreed it spikes over 250V,
and said it's "within limits" at the meter so they'll do nothing.
Questions:
1. Does the H1 expose the INSTANTANEOUS over-voltage threshold anywhere
— front panel, installer tool, or modbus register? Or is it fixed at
the G98 stage-1 point (262.2V/1s) with no user access?
2. If the DNO refuses on the grounds that their own meter reads within
limits, what actually worked for anyone here? Substation tap change?
3. Anyone seen an H1 report the two faults separately, and does the
instantaneous one log anywhere useful?
I'm not looking to disable protection — I want to know whether the
threshold is reachable at all, and what the realistic route is when the
DNO says no.
Thank you in advance for any advice given.
firmware 1.63/1.02/1.70.
Not the fault in the "Error Code 28 / Vac 10min Avg" thread — my fault
register reports "Grid Voltage Fault" (instantaneous), never "Grid 10min
Voltage Fault". They're separate bits in the same word. I proved the
10-min rule isn't my trigger: over today's 05:36-14:07 window the
sliding 10-min average was above 253V in 243/243 windows (and above 255V
in 88%). If that rule were tripping me I'd be in permanent fault, not
intermittent. So raising Vac 10min Avg 253->255 does nothing for me.
What I actually see:
- Trips occur at 259-263V instantaneous. ~100 trips on 17 Sep, 131 min
off-grid, first trip 02:08 (pitch dark — no export).
- 74.9% of all 28,723 hours since Jun 2023 had a max above 253V.
7.0% above 258V. 29 hours above 262V. All-time max 264V (17 Sep 2026).
- The night voltage is WORSE than the solar-peak voltage: 00:00-04:59
mean 255.5V vs 10:00-15:59 mean 253.2V. Nothing to do with my export —
it's over-voltage at 3am with the panels producing nothing.
DNO (Northern Powergrid) visited, measured, agreed it spikes over 250V,
and said it's "within limits" at the meter so they'll do nothing.
Questions:
1. Does the H1 expose the INSTANTANEOUS over-voltage threshold anywhere
— front panel, installer tool, or modbus register? Or is it fixed at
the G98 stage-1 point (262.2V/1s) with no user access?
2. If the DNO refuses on the grounds that their own meter reads within
limits, what actually worked for anyone here? Substation tap change?
3. Anyone seen an H1 report the two faults separately, and does the
instantaneous one log anywhere useful?
I'm not looking to disable protection — I want to know whether the
threshold is reachable at all, and what the realistic route is when the
DNO says no.
Thank you in advance for any advice given.