"Operation Mode when soc target reached" for forced discharge or forced charge schedule windows
"Operation Mode when soc target reached" if doing a forced discharge or forced charge once the soc target is reached in the window the user can select the remaining mode of operation in the schedule window ie "Self Use", "Backup/grid power", or "feed in priority".
Currently it looks like once soc target reached (for both forced charge and forced discharge) in the window it goes to backup mode i.e. feed from grid, users (not installers or agents) need the option to set the system to "Self Use", "Backup", or "feed in priority" for whatever time is left in the schedule window once the soc target is reached in the app and foxesscloud.
So for example in a forced discharge window from 18:00-21:00 with discharge soc set to 40%, with self use set as the mode of operations where no time schedule exists (user has selected "operation mode when soc target reached = self use):
At 18:00 battery starts discharge at set level of 10kwh, soc target is reached at 20:00 then remainder of mode from 20:00-21:00 is set to self use, when 21:00 hits it goes to selfuse.
example a forced charge event from 11-2pm with soc target set to 100%, with self use set as the mode of operations when no time schedule exists, but if soc target reached during 11-2pm use wants to use grid power ie select backup mode/should rename to grid priority.
at 11:00 forced charge starts, battery reaches 100% soc at 12:00 then continues to draw from grid and not go to self use until 2pm.
Ive read its in firmware for months now since Jan 2026, if so what version from fox ess will this be available?
Re: "Operation Mode when soc target reached" for forced discharge or forced charge schedule windows
Yes, this is so important for users on Flow Power or Globird. When is this going to be implemented in the FW?
So this feature is now in foxess app v2.2.18, however to see this you need to be on version 1.69 master firmware for kh10. I do like the wording used "After Charging Cut-off:" and "After Discharging Cut-Off"
Problem is 1.69 master firmware version for kh10 introduces a 63amp grid import hard limit approx 14.5kw grid import, so 10kw to battery and 4.5kw to house loads max.
On Master Firmware version 1.67 KH10 the grid import limit wasn't restricted and it could be set to 80amps and do over 17.5kw grid import. So you can do 10kw battery charging and 7.5kw house loads at same time.
FOXESS Your are reading these please remove the restriction on the grid import limit on say version 1.71 so us single phase customers on 80amp+ grid circuit can make the most of the system!!!!!
Very interested as to why the 63amp grid limit was introduced in 1.69 on KH10 as the kh10 inverter installer settings state the kh10 can be setup with a max ac current of 78.3Amps and 18000 Kw. But the grid import limit isn't about the kh10 itself it is about thee grid load to the house (but every house will have a circuit breaker limiting power to hosue, even limited by the elctricity supplier), the kh10 is protected by its own inverter circuit breaker either 80amps or 63amps max depending on country.