'G100 State 3'
Our very new installation is playing up, and we have 'G100 State 3' on the inverter. I read something about locking out so now panicking - Any ideas?
Here's what we've got:
Inverter: H1-3.0-E-G2 (Master 1.27, Slave 1.02, ARM 1.44)
Battery: EP5 (version BMS 1.004)
If relevant, we have what might be a separate issue but I mention it in case it isn't - When the battery is on, it sucks house load from grid instead of solar. Solar only seems to work to charge the battery, after which it stops generating and house continues to take from the grid. Beautifully sunny day here so this is very odd! If we turn off the battery, solar feeds the house no problem. Work mode is set to 'self use' and no charge settings are on.
Thank you in advance oh knowledgeable people!
Re: 'G100 State 3'
Unless you have a reason to be set to G100 (like an export limit), I wouldn’t expect to see any G100 errors on a 3kW inverter as it is below the G98 limit and shouldn’t need anything special.
The state 3 means that your inverter has detected a parameter grid voltage, frequency, export power etc.. that is outside of the parameters set and it will shutdown until the problem disappears - it sounds to me as if your installer has configured this incorrectly, give them a call to check it out - as I said, I really wouldn't expect to be seeing a G100 on such a small system, and if it is set then the parameters are incorrect and need to be set correctly.
Re: 'G100 State 3'
Hi Dave, thanks for your response and wisdom!
We do have an export limit- we aren't allowed to export at all to the grid currently (it's a very small grid on an island that isn't set up for this yet). So my husband set the maximum export power to 0 to prevent the export. I'm guessing these are the incorrect parameters you mentioned - we haven't been able to find instructions for setting this in the manual though - have you got a link? Or are we best talking to Fox?
Do you think this could be causing the battery problem too?
Unfortunately this is a semi-DIY situation - there's no installer on the island so we flew one over as a bit of a favour but he's had to go back now.
Re: 'G100 State 3'
There’s nothing wrong with setting the export limit to throttle the export so that should be all good, but the G100 message implies you have the wrong safety code selected - set it to G99_UK and then with the export limit set to 0 it won’t export.
You are also on older firmware, if you have installer or agent access you can update these yourself the latest versions are -
Master 1.33
Slave 1.03
Manager 1.49
Update your Master first, then Slave and then Manager
On your batteries the firmware there is also a few versions old and as these are such new batteries I would recommend updating them to latest 1.007
You can also raise a ticket via the V2 app and Fox will update the firmware for you but make sure you ask them to update the inverter and batteries.
Re: 'G100 State 3'
Hi Dave,
Thought I'd just send you my thanks.
We submitted a request for firmware update to Fox but they've not done anything (a week later) so we sorted the account and did it ourselves, along with changing to G99_UK and a hard reset after all that and.... it's working! Fabulous weekend of using the battery overnight and recharging through the day - very happy family here.
Thanks again!